Quote:
Originally Posted by macafee2
fully appreciate wont be all on at once but this week my brain is mush.
just had a phone call about a freezer, its start up current which is only a moment i grant you...... is.....66amps
macafee2
|
See post 27. That is not a problem. Just look at your continuous load. The inrush current is only milliseconds and if you had a 50 amp fuse it would not blow/trip it.
In fact you are protecting the freezer with a 13 amp fuse. You need to worry about the important things in life.