Sorry if I’ve missed this question: we have an MCB consumer unit and currently there are two 45A loops, both terminating in the kitchen. I’m moving the kitchen and laying a new loop in the (old) dining room for the cooker.
I’m very tempted by the deals on the MG5 although a glass topped ZS would be nice. Just wondering if you can fit your own 7Kw charger on a redundant shower circuit? Currently it’s 6mm but could easily change it to 10mm.
Sounds like this OLEV grant is more hassle than it’s worth?
Sent from my iPhone using Tapatalk
|
I'd recommend you change it to 10mm. If you're OK with electrical work, that would do the trick. 6mm would be marginal for long term continuous charging at 7kw.